if you check using the link to the calculator I posted previously it says 16mm is OK for 2m at 60A, amazing difference an extra 4m makes…
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
I fully agree that the cable supplied with Johns install was inadequate. But then saying it should have been 50mm2 is something I don't agree with. if you do think that, that is fine. I don't. simple as that.I was commenting on GJ installation where he has a 6m length this is very important factor, and there are many others that can cause you to de-rate the cable. The IEE on-site guide is lacking when it comes to DC installs.
And I will tell you that I think THAT is wrong. Why so I say that? As I have around 2M of 16mm2 cable on my 60A B2B and I will be replacing it with 25mm2 (or even 35mm2 just as it is easy to do) when I get round to it. as I feel there is a bit too much heat generated. it is not dangerously so by any means but as I said earlier ... heat = waste.if you check using the link to the calculator I posted previously it says 16mm is OK for 2m at 60A, amazing difference an extra 4m makes…
Ours is 90A B2B factory installed and the manufacturers recommendation is 25-35mm depending on cable run being less than 6m or less than 9m, for a 60A they go from 16mm to 35mm again depending on cable run less than 6m to 12m.No, but I have never seen a commercially produced motorhome with a 60A B2B, ours is 20A, but it also only has a lead acid leisure batter. lf you upgrade to Lithium and your B2B to 60A you need to rate the cables to suit, How would You calculate the size then? As Lenny says the sizes keep volt drop to 3% which is the normal acceptable limit.
I was using Gadget John’s Ecoflow system, the only data I had was 60A 6m and it was a return system, i.e. 2 cables (Not using chassis ground). I did use 12V but as you will see if you use 14.5v you get the same answer of 50mm. They should not have supplied such a small gauge cable and absolutely not one with an horrendous “join“ in it.so using that calculator would actually UNDERSIZE cables for some uses. use a 4mm for a Compressor Fridge on a 6M run and you will get an high voltage drop on the compressor surge and unless the battery is maybe 80% SOC, you will have a battery that is fine but a fridge that reports low voltage.
Next, for the typical B2B installation, most installers (including Professional installers) use the chassis as a common ground. Using your online calculator again, check the cable needed for a 60A B2B with a chassis return instead.
Also, you will probably have put the voltage as "12V"? You won't be driving the B2B at 12V from the alternator, but between something like 13.8 - 14.5V. That makes a fair old difference as well.
When using a tool to work out sizes, it is important to enter ALL the factors in.
Agreed. If you use a different cable size calculator you get much the same results. These also agree with my own spreadsheet calculations starting from scratch, but I don't expect that will cut much ice. These apparently OTT cable sizes for a 6m 2-way cable run are a very good reason why 12V electrics are a bad solution for high power electrics. Also why it's advised to keep the high amps cable runs as short as possible.I don't agree, his cable sizes are correct if you want to keep losses to under 3%.
Most B2B installations have much shorter cable runs than 6m, most under 2m so you could use 16 mm2.
Yes 50mm does seem over the top, and most probably won’t fit the terminals!!! The better manufacturers actually give tell you the maximum cable size, and recommended sizes per length eg Victron 12/12/30A terminal max 16mm2And I will tell you that I think THAT is wrong. Why so I say that? As I have around 2M of 16mm2 cable on my 60A B2B and I will be replacing it with 25mm2 (or even 35mm2 just as it is easy to do) when I get round to it. as I feel there is a bit too much heat generated. it is not dangerously so by any means but as I said earlier ... heat = waste.
But people are entitled to think what they want. and there are plenty of other calculators which will give different answers - some higher, some lower.
Indeed so. You cannot fit a strand thicker than a standard 16mm2 cable into a 30A Orion-Tr cable. (I always use the Pin terminal connectors with the Victron Orion 30A as the bare cables are a real pain if you need to refit a cable in situ).Yes 50mm does seem over the top, and most probably won’t fit the terminals!!! The better manufacturers actually give tell you the maximum cable size, and recommended sizes per length eg Victron 12/12/30A terminal max 16mm2
and minimum sizes on length 5m -16mm.
Good tipI always use the Pin terminal connectors with the Victron Orion 30A as the bare cables are a real pain if you need to refit a cable in situ).
For anyone looking for 16mm2 pin connectors, this is probably the best one from a reliable quality source - https://uk.rs-online.com/web/p/crimp-pin-connectors/8092366.Good tip
I did note that none of you mentioned that the rating is when the cable is in free air. If you put it in conduit/trunking or anything else that insulates it, it keeps in heat and you need to derate accordingly.it is important to enter ALL the factors in.
Also, you will probably have put the voltage as "12V"? You won't be driving the B2B at 12V from the alternator, but between something like 13.8 - 14.5V. That makes a fair old difference as well.
There is on the calculator that is being linked. Check again.Just noticed this. I think you will find it doesn't make any difference.
In this context the losses in the circuit in watts is dictated by the resistance of the cable and the current flowing in it. The formula is
W = I²R
No mention of voltage there.
Again, there is on the calculator being linked to. Rightly or wrongly, THAT calculator is the one that is under discussion to work out cable gauge? Check again.I did note that none of you mentioned that the rating is when the cable is in free air. If you put it in conduit/trunking or anything else that insulates it, it keeps in heat and you need to derate accordingly.
Also running multiple cables side by side, you also need to derate.
Both of you are partly right. W = I²R is correct, the power wasted and the voltage drop do not depend on the battery voltage. It would be the same watts wasted and voltage drop if it was a 240V supply giving out 60A.
But the percentage loss would be different. A voltage drop that's 3% of 12V (ie 0.36V) would be 2.5% of 14.5V and 0.15% of 240V. It's the principal reason houses use 240V not 12V, so they can use less copper, even though 240V is dangerous.
It plays a part in determining the cable thickness, which is the whole conversation.Correct. My point was that mentioning voltage is pointless as it plays no part in the calculations.
It doesn't. I am sorry but my memory may be a bit fuzzy on this. We had to go back to first principles on this topic and calculated the required csa of a cable required given the materials resistivity and it's temperature coefficient.It plays a part in determining the cable thickness, which is the whole conversation.
But that is exactly what we want to do.The only time the actual circuit voltage would be of interest is if you wanted to limit the voltage drop as a percentage of the source voltage.
Also, you will probably have put the voltage as "12V"? You won't be driving the B2B at 12V from the alternator, but between something like 13.8 - 14.5V. That makes a fair old difference as well.
WrongJust to be clear. This is the bit I was querying. 12v vs 14.5v will make no difference to the cable size calculations in our applications.
Wrong
Also, you will probably have put the voltage as "12V"? You won't be driving the B2B at 12V from the alternator, but between something like 13.8 - 14.5V. That makes a fair old difference as well.
Just to illustrate I will do the screenshots for you so you can see. As per my previous note, I am not that bothered, but as you feel the need to quote my posts, I feel the need to reply to correct you where you are wrong.You insisted I look at your calculator... So here we go.
@60A 12v vs 15V
View attachment 716797View attachment 716796
Or at lower current levels.
@20A 12v vs 15v
View attachment 716798View attachment 716799
If I am wrong, I would hate to see what being right means?
Using 12v or 14.5v in these calculations makes absolutely no difference.
yup, that is a fair statement from him in quite a few ways, considering how the initial post here was worded.Interesting reply from Gadget John on instagram this morningView attachment 716808
Just to illustrate I will do the screenshots for you so you can see. As per my previous note, I am not that bothered, but as you feel the need to quote my posts, I feel the need to reply to correct you where you are wrong.
OK. Imagine you don't have a 6M run but just 4M (just as likely. actually more likely). What is the effect of the voltage on your 20A demand in terms of the cable THAT calculator recommends at the two different voltages you say has no bearing on the results?
View attachment 716832View attachment 716833
Think that settles that "makes no difference" arguement?
Any link to it?Interesting reply from Gadget John on instagram this morningView attachment 716808