Good evening all,

Thanks to the wonderful information I've gathered from other threads (particulary this one) and help from DJL220 and Two on Tour I think I've finally got a plan for my upgrade.

The kit is ordered (thanks mainly to RogerIvy) and with the help of the diagrams in the post above, I've tried to map out the installation. I dont have a great amount of space in the 'garage' under bed and the diagram below is to scale.

I'm limited with Visio skills and the cabling in real life will be more ordered - but I guess it shows the general positioning.

Does it look ok to you experienced funsters? Or is it a dog's dinner? :giggle:
1726773119271.png


My main concern is whether I'm trying to get two much kit in a confined area. My plan is to sort of 'box' the install in with ply but with large mesh 'windows'. Something like this on the front and end panels...

1726773745561.png

I'd welcome any feedback.

TIA, Martin

1726773770532.png
 
Sep 13, 2019
383
941
Hertfordshire
Funster No
64,185
MH
Bailey 79-4T
Exp
Since 2019
Hi Martin
I would take the feed from you Alternator for the XS not the starter motor. I would also make sure there is ample room around the install for airflow if you are looking at boxing.
I added 2 mmpt on my install as below.
1) 100w panel (75/15)
2) 2 x 175 w panels (100/30)
Sure as they are not the same size you should do the same.
Regards
Darren
 
Upvote 0

Two on Tour

LIFE MEMBER
Sep 16, 2016
10,831
56,112
Near the junction of the A14 and A1, Cambs
Funster No
45,145
MH
Elddis Autoquest 175
Exp
Since 2010
Hi Martin
I would take the feed from you Alternator for the XS not the starter motor. I would also make sure there is ample room around the install for airflow if you are looking at boxing.
I added 2 mmpt on my install as below.
1) 100w panel (75/15)
2) 2 x 175 w panels (100/30)
Sure as they are not the same size you should do the same.
Regards
Darren

I think that Martin is referring to the starter (cab) battery on the feed for the XS.
 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
Hi Martin
I would take the feed from you Alternator for the XS not the starter motor. I would also make sure there is ample room around the install for airflow if you are looking at boxing.
I added 2 mmpt on my install as below.
1) 100w panel (75/15)
2) 2 x 175 w panels (100/30)
Sure as they are not the same size you should do the same.
Regards
Darren
Thanks Darren, apologies, I should have put starter battery - or just cab battery (y)
 
Upvote 0
Aug 13, 2017
617
888
Funster No
49,969
Might you benefit from an RCD on the inverter output too, or possibly put it downstream (if suitable) from the change over switch (relay) which should be 'break before make' also I think....that way the one RCD serves both EHU and Inverter inputs to sockets etc.....again....I think !
In terms of 'panelling' I'm intending to use clear polycarbonate sheet ( 10mm but think 5 or 6 would suffice) as it has a good fire resistance and is easy to work and very 'visual'...... and in order to maximise surface area I'm intending to use both sides and use copper studs to pass through the sheet etc where suitable.....!

Subscribers  do not see these advertisements

 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
Might you benefit from an RCD on the inverter output too, or possibly put it downstream (if suitable) from the change over switch (relay) which should be 'break before make' also I think....that way the one RCD serves both EHU and Inverter inputs to sockets etc.....again....I think !
In terms of 'panelling' I'm intending to use clear polycarbonate sheet ( 10mm but think 5 or 6 would suffice) as it has a good fire resistance and is easy to work and very 'visual'...... and in order to maximise surface area I'm intending to use both sides and use copper studs to pass through the sheet etc where suitable.....!
Thanks Ian, two great points. I like the idea of the polycarb sheet!
 
Upvote 0

bigtwin

LIFE MEMBER
Oct 29, 2009
5,714
10,971
Derby
Funster No
9,111
MH
Concorde
Exp
Since 2006
I suspect that your current solar configuration will be current limited by the 90W panel. Probably better to use a separate controller for that panel.

Ian
 
Upvote 0
Apr 26, 2015
3,321
8,006
Ottershaw
Funster No
36,067
MH
Hymer S820
Exp
First motorhome May 2021
Personally, with LifePO4, I’d fit an Ablemail AMT12-2 battery maintainer instead of the Battery Master.
Can I ask why? I have cbe battery maintainer which starts charging the engine battery once the leisure battery gets over 13.6 volts, my Fogstar Drift battery is set to float at 13.61 volts and the battery maintainer keeps the engine battery at a steady 13.1 volts providing up to 4 amps if it is required. The CBE unit is £40 the AMT12-2 is £90.

Subscribers  do not see these advertisements

 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
Hi Martin
I would take the feed from you Alternator for the XS not the starter motor. I would also make sure there is ample room around the install for airflow if you are looking at boxing.
I added 2 mmpt on my install as below.
1) 100w panel (75/15)
2) 2 x 175 w panels (100/30)
Sure as they are not the same size you should do the same.
Regards
Darren
Interesting thanks Darren. My current setup is the 90 and a 175w into a 75/15. It seems to work but I'll double check and might need to keep the 90w on the old controller. (y)
 
Upvote 0
Apr 26, 2015
3,321
8,006
Ottershaw
Funster No
36,067
MH
Hymer S820
Exp
First motorhome May 2021
You have your solar panels wired in series which will make them less efficient if partially shaded and also they will deliver less amperage then wiring them in parallel.
 
Upvote 0

Lenny HB

LIFE MEMBER
Oct 18, 2007
56,162
164,689
On the coast in West Sussex
Funster No
658
MH
Carthago Compactline
Exp
Since 2008 & many years tugging
That confused me, you have labeled your mains sockets as 12v.
I fitted a RCBO on the output of my inverter, neutral has to be grounded for a RCD/RCBO to work, not all inverters allow this.

As bigtwin says the solar output will be limited by the 90w panel. I would never connect panels in series on a Motorhome far better in parallel.

Biggest problem I had in a small space was getting tight bends on large cables.

Here is mine in an unfinished state.
1726782825059.jpeg
 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
I suspect that your current solar configuration will be current limited by the 90W panel. Probably better to use a separate controller for that panel.

Ian
Thanks Ian. I must admit, I never seem to get high wattages, even on bright and cool days. The max I've had in the last month was 152w...

1000049559.png


I actually added the 90w to give the existing 175w a little 'boost' but it seems I may have achieved the opposite!

"A fool and his money...etc"
 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
That confused me, you have labeled your mains sockets as 12v.
I fitted a RCBO on the output of my inverter, neutral has to be grounded for a RCD/RCBO to work, not all inverters allow this.

As bigtwin says the solar output will be limited by the 90w panel. I would never connect panels in series on a Motorhome far better in parallel.

Biggest problem I had in a small space was getting tight bends on large cables.

Here is mine in an unfinished state.
View attachment 952558
It's a thing of beauty already Lenny, you must have dainty fingers :LOL:

I'll do more research on the cabling of the panels and it looks like getting them parallel is a no brainer!

And good spot, I'll correct the voltage on the sockets, thanks
 
Upvote 0
Apr 26, 2015
3,321
8,006
Ottershaw
Funster No
36,067
MH
Hymer S820
Exp
First motorhome May 2021
Went off the CBE unit after having one fail costing me a starter battery.

The Ablemail is only £60.
Sorry to hear that Lenny, I hope i'd spot that if mine were to fail as the battery voltage is displayed on the b2b section of the Victron app and the Vanbitz Growler/immobiliser sends out a low voltage text as I discovered when the IP22 went to storage mode which wasn't high enough to trigger the CBE, easily fixed by raising the storage voltage to over 13.6 volts.
Re. The cost of the Ablemail, they've gone up in price unless you know where to get a discount.

 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
I suspect that your current solar configuration will be current limited by the 90W panel. Probably better to use a separate controller for that panel.

Ian

You have your solar panels wired in series which will make them less efficient if partially shaded and also they will deliver less amperage then wiring them in parallel.
So I've been giving this some thought after Ian and Chris's (and Lenny's) feedback and I have another question to ask if that's ok?

I now plan to leave the existing controller in place soley for the 90w panel and then parallel the two 175w into the new controller....

1726827625133.png


But, I'd rather not have to drill another hole in the roof so wondered if it would be possible to add the 90w as another 'string'.....

1726828008216.png


or will I have the same detriment of the 90w panel being in the same 'system'?

p.s. I'm still researching whether I can ground the neutral of the Giandel inverter!
 
Upvote 0
Apr 26, 2015
3,321
8,006
Ottershaw
Funster No
36,067
MH
Hymer S820
Exp
First motorhome May 2021
So I've been giving this some thought after Ian and Chris's (and Lenny's) feedback and I have another question to ask if that's ok?

I now plan to leave the existing controller in place soley for the 90w panel and then parallel the two 175w into the new controller....

View attachment 952662

But, I'd rather not have to drill another hole in the roof so wondered if it would be possible to add the 90w as another 'string'.....

View attachment 952668

or will I have the same detriment of the 90w panel being in the same 'system'?

p.s. I'm still researching whether I can ground the neutral of the Giandel inverter!
This may help you decide how to wire your panels, you should be able to calculate the effects on your set up using the examples shown as a guide.

Subscribers  do not see these advertisements

 
Upvote 0

bigtwin

LIFE MEMBER
Oct 29, 2009
5,714
10,971
Derby
Funster No
9,111
MH
Concorde
Exp
Since 2006
But, I'd rather not have to drill another hole in the roof so wondered if it would be possible to add the 90w as another 'string'.....
or will I have the same detriment of the 90w panel being in the same 'system'?

You’re effectively paralleling all the panels. That’s ok if they have the same voltages, otherwise the voltage generated will be limited to that of the lowest rated panel (I suspect that would be less of a compromise than when you had them in series).

However, the best solution is to use two controllers. Could you not get both sets of cables through the existing hole, perhaps with a multi-cable gland on top?

Ian
 
Upvote 0
OP
OP
L
Jun 6, 2019
104
75
Funster No
61,457
MH
C Class
Exp
Since 2019
Thanks again both. The Explorist blog post was REALLY helpful thanks.

It helps me to see actual numbers so using the basic maths in the post, it looks like I'd see a vast improvement just switching to parallel (as the max voltages are virtually the same on the Victron panels)

1726838188622.png


It also reminds me that I added the 90w panel and saw a nominal increase of 4w :rolleyes:

1726838328393.png


Hopefully my foolishness will help guide other funsters in the future!!
 
Upvote 0

bigtwin

LIFE MEMBER
Oct 29, 2009
5,714
10,971
Derby
Funster No
9,111
MH
Concorde
Exp
Since 2006
Thanks again both. The Explorist blog post was REALLY helpful thanks.

It helps me to see actual numbers so using the basic maths in the post, it looks like I'd see a vast improvement just switching to parallel (as the max voltages are virtually the same on the Victron panels)

View attachment 952717

It also reminds me that I added the 90w panel and saw a nominal increase of 4w :rolleyes:

View attachment 952718

Hopefully my foolishness will help guide other funsters in the future!!

It’s good to see learning and acquired knowledge in action.👍

Ian
 
Upvote 0
Jan 30, 2020
3,631
16,992
Mid Bedfordshire
Funster No
68,408
MH
RS Endeavour
Exp
Just a tad..
It's a thing of beauty already Lenny, you must have dainty fingers :LOL:

I'll do more research on the cabling of the panels and it looks like getting them parallel is a no brainer!

And good spot, I'll correct the voltage on the sockets, thanks

Your colour coding and wiring plan on the panels is wrong too! 😉

If you are doing series, you wire positive to negative of the next panel until you have completed the string, so you are effectively upping the voltage and reducing the amps. Useful as you need only smaller cables from the panels to the MPPT. I’ve started running my floor solar panels in series and I’m that impressed with the higher yield, I’m swapping the roof to series too! They kick in earlier and stay producing until later in the day due to higher voltage.

I’d run the pair of matched panels in series to the 100/30 and the smaller panel separately to your existing MPPT..
 
Upvote 0
Apr 26, 2015
3,321
8,006
Ottershaw
Funster No
36,067
MH
Hymer S820
Exp
First motorhome May 2021
Your colour coding and wiring plan on the panels is wrong too! 😉

If you are doing series, you wire positive to negative of the next panel until you have completed the string, so you are effectively upping the voltage and reducing the amps. Useful as you need only smaller cables from the panels to the MPPT. I’ve started running my floor solar panels in series and I’m that impressed with the higher yield, I’m swapping the roof to series too! They kick in earlier and stay producing until later in the day due to higher voltage.

I’d run the pair of matched panels in series to the 100/30 and the smaller panel separately to your existing MPPT..
Can you please let us see your comparison results as the above maths would tend to disagree with your post, also if you're going to rewire your roof panels to series, do a little test on your floor panels by putting them in partial shade and see what output you get, you can always move the floor panels but you can't easily move your roof panels out of shade.
 