Yup.I've got a terminal fuse on my Fogstar, then an isolation switch before the rest of the fuses.If a mega fuse can re establish itself I'd imagine a terminal fuse could as well.He's saying that standard fuses aren't good enough as the main fuse on your battery, it needs to be a class C fuse.
Maybe Lenny HB can comment
Apparently ordinary mega fuses under a dead short of the battery, can weld themselves back together after blowing.
Basically questionning whether mega fuses are the best optionSome insight into what it is might stimulate some responses/debate.
I’m never minded to respond to click bait YouTube videos.
Ian
Yes, they can. That’s why MRBF or T Class are recommended for LiFePO4 batteries.Apparently ordinary mega fuses under a dead short of the battery, can weld themselves back together after blowing.
They do, but that isn’t their purpose.Do our LiFePO4 batteries not have a BMS which will handle this proble
DittoYup.I've got a terminal fuse on my Fogstar, then an isolation switch before the rest of the fuses.
They might but they have a much higher interrupt capacity so it’s unlikely.If a mega fuse can re establish itself I'd imagine a terminal fuse could as well.
They’re not appropriate at all.Basically questionning whether mega fuses are the best option
Thanks for the video linkI (now) have MRBF terminal fuses on each of my Fogstar's, which are easier to fit/use and definitely a better option in my opinion, but I do still think this guy is being a little sensationalist in showing a van blowing up etc. This video explains it much clearer and identifies why the ICC of the fuse is so important, and what state they adopt when they fail.
I would have a look and see what manufacturer recommendsCan anyone recommend what size MRBF fuse would I need for a 304ah Fogstar please?
I have a 3000w Renogy inverter aswell ...
Thanks
The maximum rated output of the battery is 250a, so a fuse of 300a is fine, and this is the limit of the holders if using Blue Sea ones. Naturally your cables must also be rated to carry this current.Can anyone recommend what size MRBF fuse would I need for a 304ah Fogstar please?
I have a 3000w Renogy inverter aswell ...
Thanks
Really useful pdf. Thank you.
I've just checked mine as I didn't recall seeing a fibre washer and it seems they've changed the design since this document. The bolt is now actually isolated from the plate at the bottom so there is no need for the fibre washer at the top.
Any idea how much cumulative power you were pulling through that fuse? Just out of curiosity.I (now) have MRBF terminal fuses on each of my Fogstar's, which are easier to fit/use and definitely a better option in my opinion, but I do still think this guy is being a little sensationalist in showing a van blowing up etc. This video explains it much clearer and identifies why the ICC of the fuse is so important, and what state they adopt when they fail.
I'm not so sure that the figure of 99.9% of people using the wrong fuses as quoted by the first guy is necessarily true, but I have seen an awful lot of systems on here with Mega fuses on the batteries.
If real world evidence is needed, below is my personal experience of what can happen when you have a short circuit whilst using a correctly 'rated' (genuine) Mega fuse on lithium batteries. Not ideal and a big learning curve. I was annoyed at myself as I originally had ANL fuses, which were fine, and swapped them out for Mega simply because I preferred the holders!
View attachment 1004831
I don't know, but certainly more than enough to blow the fuse so can only assume it had bridged. Judging by the way the scorch marks are I believe this is what happened.Any idea how much cumulative power you were pulling through that fuse? Just out of curiosity.
Mike.
No, semiconductors switching is not capable to deal with kA of shor circuit or fault current, you need a fuse that is capable of few kA.Do our LiFePO4 batteries not have a BMS which will handle this problem?
What size cable?Can anyone recommend what size MRBF fuse would I need for a 304ah Fogstar please?
I have a 3000w Renogy inverter aswell ...
Thanks
35mm about 600mm in lengthWhat size cable?
Just don't copy me with the 250A. That was on a 50mm2 cable and was meant not to blow, but for an worst case scenario. Since then, I did change that to a 125A dc breaker. The multiplus at max chat only needs 100A.Thanks Raul I obviously need to change the fusing arrangement in the Moho and potentially the outside utility at home.
So a 250A T Class fuse for home?
Cable to small for a 12.8v to 3000w, add another one and fuse with 250A.35mm about 600mm in length
or just up the cable to 50mm?Cable to small for a 12.8v to 3000w, add another one and fuse with 250A.