Upgraded MPPT and now not harvesting any solar ? (7 Viewers)

Affiliate links here may earn MHF compensation

Tombola

LIFE MEMBER
Nov 21, 2020
5,198
16,648
Merseyside
Funster No
78,053
MH
Rapido 8094DF
Exp
Since 2004
not got my app, but Im sure you can drop the max current in it for now
 
Dec 2, 2019
3,877
8,561
Amersham
Funster No
67,145
MH
van conversion
Exp
Since 2019
That voltage is bonkers for a 12v system. If your panels are all equal, configure it with tho Y piece connectors in 2 series the two series in parallel. That controller will produce allot of heat to buck from 120v to 12. That voltage is for a 48v battery.
And do yourself a favour before magic smoke . Change the automotive fuse from controller to battery to a midi fuse and holder.
That fuse holder will melt eventually on 45-50amps.
 
Aug 19, 2013
3,107
4,576
Wells, Somerset
Funster No
27,611
MH
Elddis 115
Exp
since 2004
I have a similar issue, but not quite the same. The solar has never shown any charge, it just reports that it is off. Apparently it will not charge until the voltage is less than 5v below the battery voltage, which has always been above 13.3-ish since the Victron mppt controller and the 100 amp lithium LB have been installed. But the solar panel does not show any voltage output from the panel at all. I seem to remember in the dim and distant, when I had a similar situation, someone said reverse the panel polarity, which I did, and it worked immediately. I'm reluctant to try that, in case it blows a fuse or worse on the Victron controller or something. So I accessed the panel leadson the roof, pulled apart the mc3 connectors, but my little meter probes do not reach the inner pins so I can't get a reading. I'm reluctant to bin the solar panel, because the replacement cost of a Truma 100 watt is 3 or 4 times that of a cheapo Chinese one. How can I check it?
 
Aug 19, 2013
3,107
4,576
Wells, Somerset
Funster No
27,611
MH
Elddis 115
Exp
since 2004
I have a similar issue, but not quite the same. The solar has never shown any charge, it just reports that it is off. Apparently it will not charge until the voltage is less than 5v below the battery voltage, which has always been above 13.3-ish since the Victron mppt controller and the 100 amp lithium LB have been installed. But the solar panel does not show any voltage output from the panel at all. I seem to remember in the dim and distant, when I had a similar situation, someone said reverse the panel polarity, which I did, and it worked immediately. I'm reluctant to try that, in case it blows a fuse or worse on the Victron controller or something. So I accessed the panel leadson the roof, pulled apart the mc3 connectors, but my little meter probes do not reach the inner pins so I can't get a reading. I'm reluctant to bin the solar panel, because the replacement cost of a Truma 100 watt is 3 or 4 times that of a cheapo Chinese one. How can I check it?

Subscribers  do not see these advertisements

 

Tombola

LIFE MEMBER
Nov 21, 2020
5,198
16,648
Merseyside
Funster No
78,053
MH
Rapido 8094DF
Exp
Since 2004
I have a similar issue, but not quite the same. The solar has never shown any charge, it just reports that it is off. Apparently it will not charge until the voltage is less than 5v below the battery voltage, which has always been above 13.3-ish since the Victron mppt controller and the 100 amp lithium LB have been installed. But the solar panel does not show any voltage output from the panel at all. I seem to remember in the dim and distant, when I had a similar situation, someone said reverse the panel polarity, which I did, and it worked immediately. I'm reluctant to try that, in case it blows a fuse or worse on the Victron controller or something. So I accessed the panel leadson the roof, pulled apart the mc3 connectors, but my little meter probes do not reach the inner pins so I can't get a reading. I'm reluctant to bin the solar panel, because the replacement cost of a Truma 100 watt is 3 or 4 times that of a cheapo Chinese one. How can I check it?
put the probes on the ends of the cables where it enters the mppt even if you have to disconnect them
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
55,887
163,094
On the coast in West Sussex
Funster No
658
MH
Carthago Compactline
Exp
Since 2008 & many years tugging
With the panels in parallel with 4mm² you will lose approx 6%.
Ifyour were getting max output in mid June you would lose 1.e amps of your 23 not enough to worry about.
In winter if the panels were producing 6 amps you would lose 0.36 amp again not enough to worry about.
 

funflair

LIFE MEMBER
Dec 11, 2013
20,040
32,978
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
With the panels in parallel with 4mm² you will lose approx 6%.
Ifyour were getting max output in mid June you would lose 1.e amps of your 23 not enough to worry about.
In winter if the panels were producing 6 amps you would lose 0.36 amp again not enough to worry about.
Isn’t that why he said he had gone series?

Subscribers  do not see these advertisements

 
Aug 19, 2013
3,107
4,576
Wells, Somerset
Funster No
27,611
MH
Elddis 115
Exp
since 2004
put the probes on the ends of the cables where it enters the mppt even if you have to disconnect them
Sorry, didn't mention I'd already done that. I wanted to be sure that there were no other fuses or contact points between the panel and the controller. There is a fuse actually on the controller, but since the light is flashing blue I assumed it had not blown.
 
Apr 27, 2016
7,384
8,789
Manchester
Funster No
42,762
MH
A class Hymer
Exp
Since the 80s
So I accessed the panel leadson the roof, pulled apart the mc3 connectors, but my little meter probes do not reach the inner pins so I can't get a reading.
I'm not sure I should be suggesting a bodge, and I've not actually used MC3 connectors, but surely you can insert a pin or nail, something thin and metallic, that you can use as an extension to the meter probe. Obviously with higher voltages, over about 50V, you should take precautions against electric shock, wrap some tape round exposed parts etc. Especially if these panels are on a roof and you are working at height.
 
Aug 19, 2013
3,107
4,576
Wells, Somerset
Funster No
27,611
MH
Elddis 115
Exp
since 2004
I've tried that too. It's the uncertainty, because I can't see that the connection is secure. I've not even seen a flicker on the meter. Of course, it could be that the panel is knackered. Which is what I'm trying to prove! I'm thinking of cutting the solar end of the cable, if it's u.s. I'll need to change to mc4 anyway. I'll give it one more go!
 
Dec 2, 2019
3,877
8,561
Amersham
Funster No
67,145
MH
van conversion
Exp
Since 2019
I've tried that too. It's the uncertainty, because I can't see that the connection is secure. I've not even seen a flicker on the meter. Of course, it could be that the panel is knackered. Which is what I'm trying to prove! I'm thinking of cutting the solar end of the cable, if it's u.s. I'll need to change to mc4 anyway. I'll give it one more go!
It could be the connector, mc3 have been ditched long time ago as they corrode. Get mc4 staubli.

Subscribers  do not see these advertisements

 

Join us or log in to post a reply.