Upgraded MPPT and now not harvesting any solar ? (1 Viewer)

Affiliate links here may earn MHF compensation

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
Bit confused, not that it takes much these days🤭

Decided to increase the number of PV panels (see here) finally added 2 x 100w panels more wired in series as so to mange the 4mm cables with the higher voltage but maintaining the same amps, output is around 120-130v now from the panels in decent sun.

As i was close to the limits of the existing Victron 100/50 controller i decided at the same time to upgrade that to a Victron 150/45, all seemed like a straight forward swap out.

Now though i get those 120-130v coming to the controller from the panels but for some reason non of it seems to go to my batteries 🤔.

It’s all been installed for a few weeks but with some trips being moving almost every day and then the B2B taking over and some days on EHU i actually didn’t notice it. Now though as we are 4 days off-grid then i soon twigged that the batteries are not being topped up 🤷‍♂️

Main dashboard from the MPPT:

IMG_8157.png


Settings for the MPPT:

IMG_8158.png


Dashboard for the BMV-712

IMG_8159.png


So what am i doing wrong😳
 
Feb 14, 2021
4,151
9,334
Milton Keynes, UK
Funster No
79,219
MH
Burstner Lyseo 727G
Exp
3 years 30,000 miles UK and Europe.. Campsites and off Grid.
I'll let someone else diagnose your issue but I'm 120 volts is way too much. 100watts solar gives maximum of 18 volts.
 

MichaelT

LIFE MEMBER
Nov 12, 2015
3,846
7,962
Colchester
Funster No
40,159
MH
Carthago I 143 LE
Exp
Since 2016
Try turning charger enabled off then after 30 seconds on to see it will force it to bulk charge. If not disconnect the +ve solar lead and reconnect to see if it resets it. I had similar when I added a 2nd battery.
 
Sep 29, 2009
998
703
East Anglia
Funster No
8,667
MH
Roller Team
Exp
Since 2009
Blown fuse between controller and battery. Battery should read same as output from mppt, hence mppt going straight to float.
 

funflair

LIFE MEMBER
Dec 11, 2013
20,039
32,976
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
You seem to have two different battery voltages, I suspect the one that says 13.99 is wrong and is putting the controller into “float” I don’t know why it’s wrong though.
 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
Has the upgraded controller ever worked?
I bought a Victron MPPT controller and it was faulty from new...

...so was my Victron Inverter...

JJ :cool:

Not that i know of, must admit that i installed it all a few weeks back, did some basic tests ie power from the panels seemed good and then put the van away, should have done a more in depth test.
 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
Blown fuse between controller and battery. Battery should read same as output from mppt, hence mppt going straight to float.

That’s a good thought, I’ll have a look at the BMS as i assume the MPPT goes to that before the batteries.

I will check if the power is arriving to the BMS

Subscribers  do not see these advertisements

 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
Try turning charger enabled off then after 30 seconds on to see it will force it to bulk charge. If not disconnect the +ve solar lead and reconnect to see if it resets it. I had similar when I added a 2nd battery.

Ok trying that now.

It seems some times being on a site without power forces you to fix things 😂
 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
I'll let someone else diagnose your issue but I'm 120 volts is way too much. 100watts solar gives maximum of 18 volts.

It seems in line with the calculations for the 4 panels, approx 450w in total.
 

Lenny HB

LIFE MEMBER
Oct 18, 2007
55,886
163,086
On the coast in West Sussex
Funster No
658
MH
Carthago Compactline
Exp
Since 2008 & many years tugging
As Martin says different voltages, the solar says battery at 13.99v & Shunt says 13.08.
As there is no current flowing in the solar controller and over 6 amps is being taken out of the batteries it looks like the controller is not connected to the batteries.
Lose connection or fuse blown?

Or if all the panels are in series shade on one panel you will lose all output, that is why parallel is preferred for Motorhomes.

Also float float voltage is too high should be between 13.5 to 13.8 depending on battery type.
 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
Ok trying that now.

It seems some times being on a site without power forces you to fix things 😂

OK tried this twice. First time it quickly flicked to absorption and then back to float, second time it switched to bulk and then immediately back to float.

Subscribers  do not see these advertisements

 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
As Martin says different voltages, the solar says battery at 13.99v & Shunt says 13.08.
As there is no current flowing in the solar controller and over 6 amps is being taken out of the batteries it looks like the controller is not connected to the batteries.
Lose connection or fuse blown?

Or if all the panels are in series shade on one panel you will lose all output, that is why parallel is preferred for Motorhomes.

Also float float voltage is too high should be between 13.5 to 13.8 depending on battery type.

Checking any fuses from between MPPT and BMS now. Currently all the panels are in full sun, couldn’t be any stronger. Reason i went series was due to cable size, it was a compromise vs what you wrote above.

Yes just float is normally at 13.5 (factory) but just tested it at 14 to see if that would force anything, seems not.

I’m guessing it’s a fuse some where.
 
OP
OP
Ridgeway

Ridgeway

LIFE MEMBER
Mar 10, 2012
3,888
7,030
Lausanne
Funster No
20,102
MH
NiBi Arto 85E
Exp
Since 2012
Not man enough for 450 watts of panel in full sun, but you worked that out yourself 😉

Thanks Martin, think the biggest i have with me is a 30amp, lets hope it doesn’t get too sunny.

What would you suggest, 40amp once I’m back ?

Subscribers  do not see these advertisements

 

funflair

LIFE MEMBER
Dec 11, 2013
20,039
32,976
Guisborough
Funster No
29,351
MH
MORELO palace
Exp
since 2012
Thanks Martin, think the biggest i have with me is a 30amp, lets hope it doesn’t get too sunny.

What would you suggest, 40amp once I’m back ?
I think 40 should be OK but double check that the wiring looks half decent, it should on a N+B, 30 might hold as hot panels are not as efficient as cooler ones and full panel wattage is quite rare in my experience.
 