Solar Panel Isolation (2 Viewers)

Affiliate links here may earn MHF compensation
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
So to get back to original query.Switch, if i decide to fit goes between panel and controller. Not as Andy in post 9 seems to indicate between controller and battery or am i reading that post wrong??
 

andy63

Free Member
Jan 19, 2014
4,672
15,018
south shields
Funster No
29,767
MH
None
Exp
since 1990
So to get back to original query.Switch, if i decide to fit goes between panel and controller. Not as Andy in post 9 seems to indicate between controller and battery or am i reading that post wrong??
My original reply to your question was given in post #3?
I'm sorry if I've taken it a bit off topic??
Andy
Edit.. I've just looked ..post 9 was a reply to Mel.. It is usually a recommendation to fuse the output on a solar controller.. That's still relevant..whether you choose to have isolation on the panel side...which isn't generally necessary..other than convenient at times...
Andy
 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Andy no need to apologise... off topic was very informative and I did not click that you also wrote post 3. Just reread 9 and it now does make sense. Thnx
 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Sorry to keep going on but can someone please explain the settings on my controller.
It states in lithium mode it has "U2 full/trickle/storage charging 13.??v continuous. Does this not mean continuous trickle charging

Subscribers  do not see these advertisements

 
Dec 2, 2019
3,709
8,017
Amersham
Funster No
67,145
MH
van conversion
Exp
Since 2019
You can fully charge a Lfp at 3.4vpc aka 13,6v given a enough time, like the van sitting idle with no loads.
The voltage cut off given by manufacturer at 14,2- 14,4v are when you charge with a stable rate of 0,2C.
That’s a constant 20A for a 100ah battery. Do you meet that requirement? When your charging is opportunistic and NOT constant, (solar), your voltage cut off should be no higher than 13,6v if you DON’T want to charge to 100%. You should not rely on bms for everyday cycling. Is there as a fail safe And should not be used as a regulator.
Dial intonyour controller conservative voltage limits, and you get good life of the battery.
 

Attachments

  • 41AAA97D-18F9-4C50-848B-C74A64538E50.png
    41AAA97D-18F9-4C50-848B-C74A64538E50.png
    473.9 KB · Views: 15
Dec 2, 2019
3,709
8,017
Amersham
Funster No
67,145
MH
van conversion
Exp
Since 2019
If you float charge at 13,4v that’s ok, it will not put any energy in the battery, but it will supply the loads from solar, and not cycle the battery. Any higher than 13,48-13,50v it will float charge. All depends of the total loads you got during charging.
I set mine on 13,45v float (got loads to feed), and 13,65 absorb for 30mins. All set on victron controller. I don’t use the victron Lfp setting profile as for me is to high at 14,2v absorb and 13,8v float. That forces the battery to 100% charge fi toooo long. The longer you sit at high voltage, the more degradation occurs.
 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Raul.. Glad u did second post cause first went straight past me. But I get jist now. It gives 14.2/4/6v depending on settings to charge then drops to 13.??v again depending on setting. At least i think that's what you are saying
 
Dec 2, 2019
3,709
8,017
Amersham
Funster No
67,145
MH
van conversion
Exp
Since 2019
If float is at 13v that is way to low. It will cycle way to deep before it triggers the charger to pump in again.
You need a float of at least 13.4v to sustain loads. If no loads then no problem.
 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Sorry Raul.. did not put that very well. Settings are
U1 13.9v. U2 13.9v
14.2v. 13.6v
14.4v. 13.8v
14.6v. 13.6v
14.8v. 13.65v
So as all these U2 figures are above 13 .4v does that mean there will always be a trickle charge?

Subscribers  do not see these advertisements

 
Jul 14, 2019
280
190
Funster No
62,405
MH
Rapido 7086f
Exp
2007
Hi not able to afford Lithium not sure if this is the right thread to bring this up but been going though a similar dilemma so looking at AGM or Gell any comments please would be greatly received thanks
 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Thanks for your time and effort Lenny which is really appreciated And i saw those graphs in the instruction booklet. Give me an engine.. fuel injector.. carberator or anything mechanical then I your man. BUT they really don't mean a thing to me.. I have tried to make sense of them but couldn't so that is why I asked on here.
 
Dec 2, 2019
3,709
8,017
Amersham
Funster No
67,145
MH
van conversion
Exp
Since 2019
Sorry Raul.. did not put that very well. Settings are
U1 13.9v. U2 13.9v
14.2v. 13.6v
14.4v. 13.8v
14.6v. 13.6v
14.8v. 13.65v
So as all these U2 figures are above 13 .4v does that mean there will always be a trickle charge?


Yes it will. The less aggressive out of all will be the 14,2v - 13,6v combination. If you can set a 0 time for absorb, and have some draw while charging, the 13,6v is not to bad, providing your solar yield will not exceed to much your loads.
The victron charger has user defined settings, where you can set time for absorb as well. A charger that has fixed default time, is just a work around from Lead.
At 14v and up will trigger cell balancing, and will hold at high voltage the cells that are charged, till the others are catching up. This is what degrades them, add some temp in the mix and the state of health will dive.
From 13,6v to 14,4v is less than 10% energy, that is not worth it. Same for the bottom knee. At 12.4 should be the cut off with a pre alarm at 12,5v.
Below this is going to dive fast as is little energy left that’s not worth discharging. If you do, the bms will disconnect and will leave your charger without battery but solar connected. That is bad for the charger.

Subscribers  do not see these advertisements

 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Don't think my roof would take the weight of a generator??
 
Dec 22, 2018
303
235
Tasmania, Australia (northern summer in Europe)
Funster No
57,664
MH
Hymer Classic B584
Exp
Since 2019
I have the Votronic Duo Digital too. It's a good controller. I put a circuit breaker between panels and controller (inside as close to panels as possible) and a fuse in the positive between controller and battery (close to battery).

The circuit breaker is handy if I want to do work on the system or read the battery voltage without the solar charge confusing the reading. I have read from a knowledgable source those type of circuit breakers are not very good quality - made from rubbish materials and trip out of spec. He prefers to use a big fuse. Could be he is old school and has seen one fail so i t turned him off them all. So far the one I have seems ok.

You should have a fuse between any power source and battery.
 
Dec 22, 2018
303
235
Tasmania, Australia (northern summer in Europe)
Funster No
57,664
MH
Hymer Classic B584
Exp
Since 2019
Hi not able to afford Lithium not sure if this is the right thread to bring this up but been going though a similar dilemma so looking at AGM or Gell any comments please would be greatly received thanks

Probably best to start your own topic, but have a look at:

 
OP
OP
poppycamper
Apr 3, 2018
3,870
10,900
Funster No
53,151
MH
PVC
Exp
1995-2004 & 2017》
Thnx for input wtf but as I was about to reply to you you say to bowhouse about Leoch AGM's
Funnily enough I having to replace batteries after 2 years.......guess what I had to replace yes 2 100ah Leoch AGM's

Subscribers  do not see these advertisements

 
Dec 22, 2018
303
235
Tasmania, Australia (northern summer in Europe)
Funster No
57,664
MH
Hymer Classic B584
Exp
Since 2019
In particular those lead carbon ones, which would seem to deal with the disadvantages of AGM (particularly tolerance of high temperature). Just as long as you have an AGM setting on any charging equipment.
 
Last edited:
Mar 8, 2015
77
35
Leeds
Funster No
35,376
MH
Auto Trail Scout SE
Exp
Since 2015
On previous campers I just put a fuse holder in the positive wire for each of my solar panels between the panel and the solar regulator, that way I could just pull the fuse when I wanted to isolate them from the system. Do NOT put one between the solar regulator and the vehicle's battery or electroblock (or equivalent) as it could cause serious damage to the solar regulator if there is nowhere for the 'input' power to go to.
On previous campers I just put a fuse holder in the positive wire for each of my solar panels between the panel and the solar regulator, that way I could just pull the fuse when I wanted to isolate them from the system. Do NOT put one between the solar regulator and the vehicle's battery or electroblock (or equivalent) as it could cause serious damage to the solar regulator if there is nowhere for the 'input' power to go to.
Oops. I have switches between mine and the batteries so I can isolate them to prevent them from draining the battery when not in sunlight or if I’m disconnecting the batteries etc. Not that I ever really turn them off but thought when fitting it may be useful. Never thought about what would happen if the input power had no where to go. Best make sure I leave either the cab or the habitation switched on just in case. I also have fuses on the panel wiring I could pull as well if needed. Might be safer. Lol
 
Jul 6, 2016
1,547
1,265
West Sussex
Funster No
43,954
MH
Carthago Chic A clas
Exp
Since 1990
On the front face of the Votronic duo solar regulator there is a fuse.

I was wondering.......if you pull out the fuse, does this isolate the panel from the regulator ???

PS. Just curious, as I'm thinking of purchasing this product.
 
Jan 19, 2014
9,533
25,190
Derbyshire
Funster No
29,757
MH
Elddis Accordo 105
Exp
since 2014
On the front face of the Votronic duo solar regulator there is a fuse.

I was wondering.......if you pull out the fuse, does this isolate the panel from the regulator ???

PS. Just curious, as I'm thinking of purchasing this product.
No, it's in the battery circuit.

Subscribers  do not see these advertisements

 
Jul 14, 2019
280
190
Funster No
62,405
MH
Rapido 7086f
Exp
2007
Hi Richard I was thinking this too Nightmare wish I had not thought of upgrading my solar system :mad::mad:
 
Oct 5, 2012
4,282
9,569
Ayrshire
Funster No
23,166
MH
Carado T132
Exp
5 years, feel free to ask me about the Carado!!
You lost me there Mel.. That's exactly where you do put a fuse on the solar system and the ones ive done the instructions tell you to fuse the output side of the controller..
The input or panel side is protected anyway and instructions don't generally ask for a fuse there... But as you have said it can be a handy way of isolating the panels?
Andy
I believe in putting a fuse inline on the + output from a solar panel as there supposedly have been fires caused by runaway panels and the regulator has not tripped them out. So an extra fuse is a good idea, as is treating a solar panel like a live battery, so in my book it requires a fuse before going into anything else.
 
Jan 19, 2014
9,533
25,190
Derbyshire
Funster No
29,757
MH
Elddis Accordo 105
Exp
since 2014
I believe in putting a fuse inline on the + output from a solar panel as there supposedly have been fires caused by runaway panels and the regulator has not tripped them out. So an extra fuse is a good idea, as is treating a solar panel like a live battery, so in my book it requires a fuse before going into anything else.
In my book, the more the merrier (amps). Perhaps these runaway panels are better than normal panels, and could attract a premium? ? ?
 

andy63

Free Member
Jan 19, 2014
4,672
15,018
south shields
Funster No
29,767
MH
None
Exp
since 1990
I believe in putting a fuse inline on the + output from a solar panel as there supposedly have been fires caused by runaway panels and the regulator has not tripped them out. So an extra fuse is a good idea, as is treating a solar panel like a live battery, so in my book it requires a fuse before going into anything else.
hmm thats a new one on me.. runaway panels..:unsure:
as I said i dont see any real advantage in fusing the panel side other than a convenient way of isolation..
the controller has adequate protection built in... yes a fuse is an additional level but to be useful would need to be a small one as all it would be protecting is the controller..
but using that as an example how many fuses or levels of protection do you need in case one doesn't work.. we are talking about a solar installation here...
the short circuit current of most panels and installations could be more than coped with by the wirings used without any danger to the wiring... not like the average leisure battery where the short circuit current would be a danger..
my view.. we may have to agree to differ (y)
Andy
 
Apr 27, 2016
7,085
8,329
Manchester
Funster No
42,762
MH
A class Hymer
Exp
Since the 80s
And i saw those graphs in the instruction booklet. Give me an engine.. fuel injector.. carberator or anything mechanical then I your man. BUT they really don't mean a thing to me.. I have tried to make sense of them but couldn't so that is why I asked on here.
These graphs are not in fact the charging profile graphs. They are graphs of the how the absorption voltage (U1) and float voltage (U2) vary with temperature. For LiFePO4, they don't vary at all - they cut off when the temperature gets too high or too low, but otherwise they are constant.

Subscribers  do not see these advertisements

 

Join us or log in to post a reply.

To join in you must be a member of MotorhomeFun

Join MotorhomeFun

Join us, it quick and easy!

Log in

Already a member? Log in here.

Latest journal entries

Funsters who are viewing this thread

Back
Top