EHU sometimes trips either shore ore house units or van control units. (4 Viewers)

Affiliate links here may earn MHF compensation
Nov 1, 2023
26
26
Christchurch, UK
Funster No
99,642
MH
Fiat Ducato Van
Exp
Since 2011
Firstly, I am useless with electricity. On recent Europe trips I cannot get power to the van as something trips, I had this looked at by a van electrical specialist (not impressed), and then by my friendly local electrician who I have found really reliable. After exhaustive checks and a few socket replacements it seemed to be ok. I have just tried it before I go away and no power, house consumer unit tripped out. Unplugged and repeated and all OK. Has anyone any idea what might be the problem .
Thanks Funsters.
 

meanders

Funster - Life Member
LIFE MEMBER
Jun 28, 2008
3,255
11,598
Ipswich, Suffolk
Funster No
3,075
MH
C class
Exp
Since 2004
Could be many things, but most likely to be
  • Fridge going into defrost mode and the element has got damp.
  • Water heater similar thermostat faulty or leaking,
  • Battery charger faulty.
  • Something else that is plugged in that does not operate the whole time.
  • Possibly the lead

Most of those as already suggested..

If you can. turn off everything but leave it plugged in, does the trip drop? Then plug in things one at a time leaving a hour or so between each until it does drop. Even then you cannot be absolutely sure its the last item plugged in unless you unplug everything else again and see if it drops again.

Intermittent faults are the worst to find.
 
Upvote 0
Sep 3, 2012
8,035
27,444
Cheshire
Funster No
22,759
MH
C Class Elddis 175
Exp
8+ years
Just make sure that everything that runs from the ehu is switched off in the van before you connect to the ehu. Then start to turn on your 240v items to determine when it trips. Or what causes it to trip.On some sites there is only enough power to run a fridge or charge your batteries (6 amps) anything else will cause can overload and hence a trip.
You may have to juggle what you have on.
 
Upvote 0

pappajohn

LIFE MEMBER
Aug 26, 2007
43,827
53,357
Dark side of the moon
Funster No
172
Exp
Since 2005
A 2nd vote for the lead.
If it's all been checked by two separate electricians and found ok it can only be the lead.
Corroded or loose wire in either plug or possible damage, either visible or not, along the length of the lead.
 
Upvote 0
Apr 9, 2024
151
367
Funster No
102,307
MH
Timberland Endeavour
I had a similar problem after fitting a socket for a microwave. When I plugged the EHU in the post breaker dropped out. After loads of checks narrowed it down to the brand new socket I had fitted. Replaced it with an old one (I knew I had one but couldn't find it!) everything was ok again.
New socket went back to B&Q for a refund.
Been perfect since.
Cheers, Dave
 
Upvote 0
Mar 9, 2021
402
1,473
Essex, UK
Funster No
79,646
MH
C Class
Exp
Since 2014
My experience was the big blue plastic connectors on the EHU lead and on the external power socket
I had assumed (wrongly) that they were waterproof
They filled up with water and tripped out the house and MH
The fix was easy, dry out everything and reassemble with lots of mastic sealant at cable entries and where the plastic bits join together
No more problems
Good luck

Subscribers  do not see these advertisements

 
Upvote 0
OP
OP
G
Nov 1, 2023
26
26
Christchurch, UK
Funster No
99,642
MH
Fiat Ducato Van
Exp
Since 2011
Upvote 0
OP
OP
G
Nov 1, 2023
26
26
Christchurch, UK
Funster No
99,642
MH
Fiat Ducato Van
Exp
Since 2011
Could be many things, but most likely to be
  • Fridge going into defrost mode and the element has got damp.
  • Water heater similar thermostat faulty or leaking,
  • Battery charger faulty.
  • Something else that is plugged in that does not operate the whole time.
  • Possibly the lead

Most of those as already suggested..

If you can. turn off everything but leave it plugged in, does the trip drop? Then plug in things one at a time leaving a hour or so between each until it does drop. Even then you cannot be absolutely sure its the last item plugged in unless you unplug everything else again and see if it drops again.

Intermittent faults are the worst to find.
I have tried this but I might switch off the battery charger as not tried that.
 
Upvote 0

Westbarn1

LIFE MEMBER
Sep 25, 2019
561
902
Norwich
Funster No
64,720
MH
Hymer BMC-T 600
Exp
Newbie
Poor power supply on site abroad maybe , had similar on a site at Salamanca recently for 3 nights, power was fine overnight, but as soon as everyone woke up in the morning it was gone for the day and then returned again late evening.
 
Upvote 0
OP
OP
G
Nov 1, 2023
26
26
Christchurch, UK
Funster No
99,642
MH
Fiat Ducato Van
Exp
Since 2011
A 2nd vote for the lead.
If it's all been checked by two separate electricians and found ok it can only be the lead.
Corroded or loose wire in either plug or possible damage, either visible or not, along the length of the lead.
It is a new lead so should be OK, same problem with the old lead.

Subscribers  do not see these advertisements

 
Upvote 0
Apr 27, 2016
7,438
8,886
Manchester
Funster No
42,762
MH
A class Hymer
Exp
Since the 80s
It is possible to narrow down the fault a bit. There are two kinds of trip switch, and they trip for two different reasons. A hookup post, house consumer unit or MH consumer unit will usually have at least one of each type.

An RCD has a 'Test' button, and protects against small leakages to earth, and electric shock. It can trip due to water in a plug or socket, slightly failed heater element etc. It's the most likely one to trip, I think. It doesn't protect against excessive current.

An MCB doesn't have a 'Test' button, and protects against excessively high current, for example if the live and neutral accidentally touch together creating a short circuit. It doesn't protect against earth leakage.

Usually a consumer unit will have one RCD, and one or more MCBs. Usually only one of these will trip. Did the RCD trip, or one of the MCBs?

In the motorhome consumer unit, switch off all the MCBs, and just switch on the RCD. If it trips, then there's leakage on the wire up to or inside the consumer unit. If it doesn't trip, turn on the MCBs one at a time, and see which one causes the RCD to trip. That will tell you which circuit is causing the problem.
 
Last edited:
Upvote 0