Hi, I just happened on this brilliant site! Thanks for posting this, mine has just blown and hopefully I will be able to sort it. Did you solder the new fuse directly onto the board or onto the end stems of the old fuse?For all the fellow mh'ers who find their Alde control panel blank and who are told they need a new PCB board (at a cost of £280)! Please read this thread and the cost of repair will be considerably less at £0.59p!
Last week whilst in Italy I woke up to find my control panel blank and no sign of life at all. If you google this problem many people are told to first check the 2 glass 20mm fuses which are under the inspection cover at the top of your boiler (F1 and F3) which are 3.15amp. They are in little green fuse holders. Most of the time you will find these fuses are perfect and not blown and you will be told you need a new PCB. NOT THE CASE.
More likely it will be fuse F2 (a 90 degree non resettable thermal fuse) which in Alde great wisdom decided to solder onto the PCB and not make it resettable. This fuse is directly below the right hand side glass fuse. Thermal fuses degrade over time so you will most likely come across this problem if your boiler is a few years old and a good income stream for Alde.
If you are a competent diy'er then you can replace this fuse by re-soldering a new thermal fuse onto the PCB. Unfortunatly I didn't have a replacement with me so as a temporary measure I removed the PCB which is an easy job:
First remove the grey cover by unscrewing the top retaining screw and 2 on the side and remove. You will now be able to see the PCB board which will look like this:
View attachment 167032
Remove the brown, blue, black, red and grey wires from the left side, the three white connectors on the right side and the 3 black wires from the bottom relay. Make a note of where they go. Next undo a hex screw to the left of the PCB board but do not remove (fastens the heat sink to the casing) Now unclip the PCB board and remove. Now you can see the thermal fuse just below the white connector:
View attachment 167041
Test the fuse by setting your multimeter to ohms and test for continuity and more than likely the fuse will have blown (no continuity). As a temporary measure if you do not have a thermal fuse just cut the fuse as close to the fuse as possible and leave the tail wires in place and using a wire with crocodile clips just join them together. Remember this is a TEMPORARY measure until you can replace with a thermal fuse:
View attachment 167043
You can order the thermal fuses from here:
-Broken Link Removed-
Luckily I had a friend who was travelling my way so they brought the fuses for me.
View attachment 167055
So when you have a replacement thermal fuse, remember that they are rated at 93 degrees centigrade therefore when soldering be very careful not to blow the fuse with the soldering iron. I placed crocodile clips onto the tails to dissipate the heat and soldered one end:
View attachment 167056
Before soldering the other tail I tested the fuse to make sure it was ok. I then soldered the other tail:
View attachment 167057
1 hour later and all is working.
View attachment 167058
Hope this helps.
Just out of interest if your not confident with a soldering iron,a fellow funster recently had a complete 3010 circuit board for sale £50 I think?.Hi, I just happened on this brilliant site! Thanks for posting this, mine has just blown and hopefully I will be able to sort it. Did you solder the new fuse directly onto the board or onto the end stems of the old fuse?
Thanks, I got it sorted, soldered onto the board. All working perfectly again! Saved myself at least €350!I soldered directly onto the board![]()
Thanks, I have it sorted though, all working perfectly again! Saved myself €350 at least!Just out of interest if your not confident with a soldering iron,a fellow funster recently had a complete 3010 circuit board for sale £50 I think?.
You just saved me $1,000! I was told by a service professional that I had to replace the whole board. I asked about the thermal fuse, and he said that the whole board needed to be replaced, it would cost me around a $1,000 he told me. So I thought nothing ventured, nothing gained. And I ordered 2 Alde thermal fuses, one extra for 'just in case'. By way of testing I just hung the new one around the old one, and VOILA, the control panel lit up just beautifully! It WAS just the thermal fuse. I have not soldered it in, I have never soldered, this would not be a good one to learn on. My question is, could I just wrap the new fuses' wires around the old fuses' wires? I'm wondering about the longevity of such a solution.For all the fellow mh'ers who find their Alde control panel blank and who are told they need a new PCB board (at a cost of £280)! Please read this thread and the cost of repair will be considerably less at £0.59p!
Last week whilst in Italy I woke up to find my control panel blank and no sign of life at all. If you google this problem many people are told to first check the 2 glass 20mm fuses which are under the inspection cover at the top of your boiler (F1 and F3) which are 3.15amp. They are in little green fuse holders. Most of the time you will find these fuses are perfect and not blown and you will be told you need a new PCB. NOT THE CASE.
More likely it will be fuse F2 (a 90 degree non resettable thermal fuse) which in Alde great wisdom decided to solder onto the PCB and not make it resettable. This fuse is directly below the right hand side glass fuse. Thermal fuses degrade over time so you will most likely come across this problem if your boiler is a few years old and a good income stream for Alde.
If you are a competent diy'er then you can replace this fuse by re-soldering a new thermal fuse onto the PCB. Unfortunatly I didn't have a replacement with me so as a temporary measure I removed the PCB which is an easy job:
First remove the grey cover by unscrewing the top retaining screw and 2 on the side and remove. You will now be able to see the PCB board which will look like this:
View attachment 167032
Remove the brown, blue, black, red and grey wires from the left side, the three white connectors on the right side and the 3 black wires from the bottom relay. Make a note of where they go. Next undo a hex screw to the left of the PCB board but do not remove (fastens the heat sink to the casing) Now unclip the PCB board and remove. Now you can see the thermal fuse just below the white connector:
View attachment 167041
Test the fuse by setting your multimeter to ohms and test for continuity and more than likely the fuse will have blown (no continuity). As a temporary measure if you do not have a thermal fuse just cut the fuse as close to the fuse as possible and leave the tail wires in place and using a wire with crocodile clips just join them together. Remember this is a TEMPORARY measure until you can replace with a thermal fuse:
View attachment 167043
You can order the thermal fuses from here:
-Broken Link Removed-
Luckily I had a friend who was travelling my way so they brought the fuses for me.
View attachment 167055
So when you have a replacement thermal fuse, remember that they are rated at 93 degrees centigrade therefore when soldering be very careful not to blow the fuse with the soldering iron. I placed crocodile clips onto the tails to dissipate the heat and soldered one end:
View attachment 167056
Before soldering the other tail I tested the fuse to make sure it was ok. I then soldered the other tail:
View attachment 167057
1 hour later and all is working.
View attachment 167058
Hope this helps.
Did you ever resolve this ? (and I realise you never actually joined, but you 'might' get notifications still?) it might be helpful for others if you can offer your solution?Hi There, We have one of the control boards that has been brought to us for repair. We have identified the exact fault above but in addition what we think is a capacitor missing, which in your image that you are testing the continuity in is located directly to the right of the "F2" symbol on the board and left of the label "JP14". Aldel of course refuse to tell us what size this is so was wondering if anyone had one of these boards and could tell us what that component size is so we can replace it and save the owner a fortune for not having to splash out on a new board.
Just had mine replaced 3 weeks agoFor all the fellow mh'ers who find their Alde control panel blank and who are told they need a new PCB board (at a cost of £280)! Please read this thread and the cost of repair will be considerably less at £0.59p!
Last week whilst in Italy I woke up to find my control panel blank and no sign of life at all. If you google this problem many people are told to first check the 2 glass 20mm fuses which are under the inspection cover at the top of your boiler (F1 and F3) which are 3.15amp. They are in little green fuse holders. Most of the time you will find these fuses are perfect and not blown and you will be told you need a new PCB. NOT THE CASE.
More likely it will be fuse F2 (a 90 degree non resettable thermal fuse) which in Alde great wisdom decided to solder onto the PCB and not make it resettable. This fuse is directly below the right hand side glass fuse. Thermal fuses degrade over time so you will most likely come across this problem if your boiler is a few years old and a good income stream for Alde.
If you are a competent diy'er then you can replace this fuse by re-soldering a new thermal fuse onto the PCB. Unfortunatly I didn't have a replacement with me so as a temporary measure I removed the PCB which is an easy job:
First remove the grey cover by unscrewing the top retaining screw and 2 on the side and remove. You will now be able to see the PCB board which will look like this:
View attachment 167032
Remove the brown, blue, black, red and grey wires from the left side, the three white connectors on the right side and the 3 black wires from the bottom relay. Make a note of where they go. Next undo a hex screw to the left of the PCB board but do not remove (fastens the heat sink to the casing) Now unclip the PCB board and remove. Now you can see the thermal fuse just below the white connector:
View attachment 167041
Test the fuse by setting your multimeter to ohms and test for continuity and more than likely the fuse will have blown (no continuity). As a temporary measure if you do not have a thermal fuse just cut the fuse as close to the fuse as possible and leave the tail wires in place and using a wire with crocodile clips just join them together. Remember this is a TEMPORARY measure until you can replace with a thermal fuse:
View attachment 167043
You can order the thermal fuses from here:
-Broken Link Removed-
Luckily I had a friend who was travelling my way so they brought the fuses for me.
View attachment 167055
So when you have a replacement thermal fuse, remember that they are rated at 93 degrees centigrade therefore when soldering be very careful not to blow the fuse with the soldering iron. I placed crocodile clips onto the tails to dissipate the heat and soldered one end:
View attachment 167056
Before soldering the other tail I tested the fuse to make sure it was ok. I then soldered the other tail:
View attachment 167057
1 hour later and all is working.
View attachment 167058
Hope this helps.
Clever guyFor all the fellow mh'ers who find their Alde control panel blank and who are told they need a new PCB board (at a cost of £280)! Please read this thread and the cost of repair will be considerably less at £0.59p!
Last week whilst in Italy I woke up to find my control panel blank and no sign of life at all. If you google this problem many people are told to first check the 2 glass 20mm fuses which are under the inspection cover at the top of your boiler (F1 and F3) which are 3.15amp. They are in little green fuse holders. Most of the time you will find these fuses are perfect and not blown and you will be told you need a new PCB. NOT THE CASE.
More likely it will be fuse F2 (a 90 degree non resettable thermal fuse) which in Alde great wisdom decided to solder onto the PCB and not make it resettable. This fuse is directly below the right hand side glass fuse. Thermal fuses degrade over time so you will most likely come across this problem if your boiler is a few years old and a good income stream for Alde.
If you are a competent diy'er then you can replace this fuse by re-soldering a new thermal fuse onto the PCB. Unfortunatly I didn't have a replacement with me so as a temporary measure I removed the PCB which is an easy job:
First remove the grey cover by unscrewing the top retaining screw and 2 on the side and remove. You will now be able to see the PCB board which will look like this:
View attachment 167032
Remove the brown, blue, black, red and grey wires from the left side, the three white connectors on the right side and the 3 black wires from the bottom relay. Make a note of where they go. Next undo a hex screw to the left of the PCB board but do not remove (fastens the heat sink to the casing) Now unclip the PCB board and remove. Now you can see the thermal fuse just below the white connector:
View attachment 167041
Test the fuse by setting your multimeter to ohms and test for continuity and more than likely the fuse will have blown (no continuity). As a temporary measure if you do not have a thermal fuse just cut the fuse as close to the fuse as possible and leave the tail wires in place and using a wire with crocodile clips just join them together. Remember this is a TEMPORARY measure until you can replace with a thermal fuse:
View attachment 167043
You can order the thermal fuses from here:
-Broken Link Removed-
Luckily I had a friend who was travelling my way so they brought the fuses for me.
View attachment 167055
So when you have a replacement thermal fuse, remember that they are rated at 93 degrees centigrade therefore when soldering be very careful not to blow the fuse with the soldering iron. I placed crocodile clips onto the tails to dissipate the heat and soldered one end:
View attachment 167056
Before soldering the other tail I tested the fuse to make sure it was ok. I then soldered the other tail:
View attachment 167057
1 hour later and all is working.
View attachment 167058
Hope this helps.
Sounds like you need the system bleeding and topping up, never had any noise from any of mine?I had exactly the same problem and repaired the same way, well done. Will never have this type of heating again as found the noise of the continuous expansion and contraction of the radiators very annoying.