well spotted.. didn't look at the MCB typeType C is more suitable for industrial applications where as type B is better for domestic applications.
I would return and have the MCBs changed to B type.. but keep the RCD .Lenny HB and scotjimland
Thank you both for your replies and advice.
Would you recommend that I return the consumer unit and purchase something more suitable?
. My daughter bought it for me from Amazon. She's seeing if she can return it.
VACANON Garage Consumer Unit 2 Way RCD Circuit Breaker Panel Garage Caravan Consumer Unit Anti-leakage Fuse Box 40A 30mA RCD 2MCB 6A+ 16A https://www.amazon.co.uk/dp/B0BWN92VJN/?tag=mhf04-21If they are difficult about a return, how is it described? If it's anything domestic it doesn't really meet that description.
Yes that will be fineLenny HB and scotjimland
Again, thanks. My daughter bought it for me from Amazon. She's seeing if she can return it.
I'm only adding 2x sockets for my 500W. Inverter. Can I just have one Type B MCB feeding both sockets radially, and get a Type B 40ms 30mA RCD?
Those are type C.VACANON Garage Consumer Unit 2 Way RCD Circuit Breaker Panel Garage Caravan Consumer Unit Anti-leakage Fuse Box 40A 30mA RCD 2MCB 6A+ 16A Amazon product ASIN B0BWN92VJN
I couldn't see that in the online description.Those are type C.
Thanks Lenny.Yes that will be fine
look at the photos.I couldn't see that in the online description.
Ah, I see ..... C6, C16, C40.look at the photos.
sorry for the late reply - I've been busy today.Sorry to bear bad news, but you need to know that a standard UK garage consumer unit is totally unsuitable for a motorhome/campervan electrics consumer unit. For a start, the MCBs are both single pole, and they need to be double-pole, or at least 1P+N.
Not only that, but the RCD looks like it's single pole switching, not double pole, and that is definitely more serious.
You will struggle to find double-pole MCBs and RCDs in the UK in DIY stores, you need to go to specialist stores like CEF. Hookup Connection units for connecting caravans are usually OK though.
Again, sorry for the late reply.And I may add, the often confusion mix up: type / curve.
RCD has a type rating, mcb a curve rating or, rcbo has both. Don’t mix the mcb breaking curve with the rcd type disconnect. Both mean different things.
Type B rcd detects ac and dc current leakage, so it’s used where AC and DC exists in a system, ie. inverters. Type C rcd does detect AC but only pulsing DC, so less DC detection.
On mcb’s or breakers, the B has less delay time for tripping on the rated current, where a C curve will allow for some sustained surge above the rated current before breaking. Both will protect the conductor if sized aproprietly.
Now, on a 500w inverter, I would personally have a C3 or B3 mcb for over current protection. The 500w Victron is double insulated, no neutral, and no rcd functionality.
Inverters are an isolated output so an RCD is not really necessary. To use an RCD with an inverter one side of the output has to be grounded.Do people just plug into the 13A Socket(s) on their Inverter, with no additional protection?
The link that Raul posted earlier in the year includes this modification to link the Earth and Neutral, which is what I had intended to doInverters are an isolated output so an RCD is not really necessary. To use an RCD with an inverter one side of the output has to be grounded.
Raul pointed out in an eairler post your inverter does not have a grounded output so you need to check the manual to see if it is OK to ground one side.
..........MCB's are not essential on an inverter as the electronics in the inverter will shut it down probably before the MCB trips but an RCD is good idea providing one side of the inverter output is grounded, Victron's are as standard
Inverters are an isolated output so an RCD is not really necessary. To use an RCD with an inverter one side of the output has to be grounded.
Raul pointed out in an earlier post your inverter does not have a grounded output so you need to check the manual to see if it is OK to ground one side.
In view of these and other comments, is it sufficient for me to install a double pole isolator, and double pole RCD, and rely on the inverter to shut down any overload?The link that Raul posted earlier in the year includes this modification to link the Earth and Neutral, which is what I had intended to do
You can do the PE bond for sure, and will enable the rcd to work properly. But you have to be mindful this will render the double insulation properties of the inverter. The more important protection you need to concentrate at, is over current protection. If it was a larger inverter with possibility to run various bigger things I would bond the neutral. But for a small 500va double insulated the over current protection will be enough. And no more than a 3A mcb, otherwise will never trip.In view of these and other comments, is it sufficient for me to install a double pole isolator, and double pole RCD, and rely on the inverter to shut down any overload?
It will only be for occasional use. Charging my e-bike battery and powering my Starlink dish when off-grid. Most things work/charge from 12v or USB...... What are you using this inverter for?
Thank you!! ( ..... and to all the others who contributed to this thread)Wire a 3 pin plug to a socket, put a 3A fuse in the plug, plug it in the inverter, and use that socket. Job done.
I like the socket with 3A fused plug solution. I know you aren't going to use an RCBO, but thought I'd point out that the 'DP RCBO' in your link is not in fact a double pole RCBO. There is a neutral wire connected to it, but that is simply for ensuring the RCD functionality works. When it trips, it only switches off the live wire, not the neutral wire.In my research last night, I was reading about RCBOs. As I will only have 1x radial circuit, could I just use a 2-Pole Isolation switch together with a 2-Pole RCBO, such as this?
DP RCBO