Been in Spain for two weeks and everything was working fine with the new Fogstar 280Ah LiFePO4 battery. Tonight power cut out and is only capable of discharging enough to run the fridge electrical for gas. Turn on any lights and the discharging stops. I then have to turn it on and off again. It keeps coming up with an over current charging alarm but I’m stationary, no solar now and not connected to electric. Cell voltages look unusual to what they have been. Chargers are eviction Orion xs and MPPT 100/30 all set up to recommended profile from Fogstar support.

Any ideas would be appreciated?



IMG_0593.webp

IMG_0594.webp
 
Also has now over current discharge. Not sure how currently only have an 80A fuse directly off battery and it’s capable of 250A



IMG_0595.webp
 
Been in Spain for two weeks and everything was working fine with the new Fogstar 280Ah LiFePO4 battery. Tonight power cut out and is only capable of discharging enough to run the fridge electrical for gas. Turn on any lights and the discharging stops. I then have to turn it on and off again. It keeps coming up with an over current charging alarm but I’m stationary, no solar now and not connected to electric. Cell voltages look unusual to what they have been. Chargers are eviction Orion xs and MPPT 100/30 all set up to recommended profile from Fogstar support.

Any ideas would be appreciated?



View attachment 1026332

View attachment 1026333
It appears the charging function is set to OFF. Maybe because of the over current alarm. Are you able to turn to ON the charging slide button in the app?
 
It turns off the discharging at less than 6a draw..! Think I might be limited..



IMG_0596.webp

IMG_0597.webp
 
I can then turn it back on again. So able to run the fridge at least off gas. But not much else. Will try to contact Fogstar tomorrow.
 
We too are in Spain, but with Fogstar Eco batteries, ie, minus any Bluetooth connection to the batteries, other than from the Victron gear.
We are sat at 13.15v and at 58% SOC, so from your second photo, if the figures are correct, there is something wrong going on elsewhere.

Screenshot_20250311_201446.webp


HTH,

Jock. :)

Subscribers  do not see these advertisements

 
I'm sure some of the auto electricians will help. If it was me I'd check fuses and connections on battery and electric circuits. I'd isolate as many things as I could and try each one individually. Then I'd isolate battery for 15mins if no difference I'd be asking folk on here. I have a fogstar but never had any problems. Is the app having a wobbler?
 
That cell imbalance seems huge. Three cells almost full and one cell almost empty.
 
That is a very unbalanced battery, with 300mV deviation. When you discharge, the low cell protection kicks in, and activates over current discharge. When you charge, the high cells hits the upper limit and activates the over current charge.
Catch 22, the way to help this massive imbalance, is to limit discharge, and apply a small charge 2-3A. That will bring the total voltage up, and the balancing will kick in. You need to spend some time in this state to allow the low cell to catch up.
Heavy discharge will hammer the low cell, and high charge will trigger the high cells into protection.
Just small a current to bring the battery to about 13.6v -13.8v max.
If the charging stops because the higher cells, stop charging, let it rest and repeat. It's a tedious process.

Subscribers  do not see these advertisements

 
Would plugging into a ehu to charge help balance cells worth a try?
 
Would plugging into a ehu to charge help balance cells worth a try?
No it won't, it will trip the high cells and cut charging. You need very small charging current to allow the low cell to catch up.
After the deviation has come down, then ehu charger will help.
 
I didn't see but have noted the explanation,

Subscribers  do not see these advertisements

 
That is a very unbalanced battery, with 300mV deviation. When you discharge, the low cell protection kicks in, and activates over current discharge. When you charge, the high cells hits the upper limit and activates the over current charge.
Catch 22, the way to help this massive imbalance, is to limit discharge, and apply a small charge 2-3A. That will bring the total voltage up, and the balancing will kick in. You need to spend some time in this state to allow the low cell to catch up.
Heavy discharge will hammer the low cell, and high charge will trigger the high cells into protection.
Just small a current to bring the battery to about 13.6v -13.8v max.
If the charging stops because the higher cells, stop charging, let it rest and repeat. It's a tedious process.
Sounds a good idea will limit the charge current on the Orion xs and maybe turn off solar
 
That is a very unbalanced battery, with 300mV deviation. When you discharge, the low cell protection kicks in, and activates over current discharge. When you charge, the high cells hits the upper limit and activates the over current charge.
Catch 22, the way to help this massive imbalance, is to limit discharge, and apply a small charge 2-3A. That will bring the total voltage up, and the balancing will kick in. You need to spend some time in this state to allow the low cell to catch up.
Heavy discharge will hammer the low cell, and high charge will trigger the high cells into protection.
Just small a current to bring the battery to about 13.6v -13.8v max.
If the charging stops because the higher cells, stop charging, let it rest and repeat. It's a tedious process.
How would it get that unbalanced as it is a very new battery and is charged by Orion XS and a solar controller with lithium profile?
 
What app are you using to read the bms. If you go into the one you are using can you turn off the balance on charging option. That should let the cells balance on their own.

Subscribers  do not see these advertisements

 
The app is the default Fogstar system.

Control of any charging of individual cell(s) will not be possible by default. Fogstar techy bods might be able to give added access.

But for a cell group to be so badly out of sync after only 4 cycles suggests a fundamental problem in the battery itself, especially if that is causing shutdowns. I think contacting Fogstar must be a way forward as I suspect a rare occasion where there will be a warranty issue where cells are behaving abnormally.
 
What app are you using to read the bms. If you go into the one you are using can you turn off the balance on charging option. That should let the cells balance on their own.
If bms has that function certainly do that, it will speed the process of balancing.
 
What app are you using to read the bms. If you go into the one you are using can you turn off the balance on charging option. That should let the cells balance on their own.
The Fogstar app. Don’t see an option for this.
 
Good luck. Our friends are in Spain with us and they too have a problem. Their Fogstar bms has shut their battery down. They too are waiting for a call back from Fogstar uk.
 
Good luck. Our friends are in Spain with us and they too have a problem. Their Fogstar bms has shut their battery down. They too are waiting for a call back from Fogstar uk.
Did you buy them together? Maybe a faulty batch.