Blue Sea Systems Mrbf (cube) Fuses

Joined
Oct 24, 2009
Posts
120
Likes collected
188
Location
Perth, Scotland
Funster No
9,024
MH
PVC
Exp
30+ years
The following were recommended to me so I use them on my lithium batteries. 80A rated


On a 47A load running for 5 minutes the fuse/assembly is too hot to touch.

With that load the voltage at + terminal on battery was 12.27v and voltage at the load end of cube fuse was 11.83v. ie 20.68W loss as unwanted heat!

Sounded like great protection to me when recommended but ............

The whole assembly is correctly installed and torqued and the loss is across the fuse.
 
Last edited:
Oh that’s interesting. I was going to get a 250a one when I do my lithium upgrade but may just stick with a mega fuse
 
The following were recommended to me so I use them on my lithium batteries. 80A rated


On a 47A load running for 5 minutes the fuse/assembly is too hot to touch.

With that load the voltage at + terminal on battery was 12.27v and voltage at the load end of cube fuse was 11.83v. ie 20.68W loss as unwanted heat!

Sounded like great protection to me when recommended but ............

The whole assembly is correctly installed and torqued and the loss is across the fuse.
not that unusual to have very hot localised areas - I used to get >100C on the connection to a 300A ANL Fuse Holder (actually distorted the holder with the heat so I changed to a Mega Fuse setup instead).
But that voltage drop across the fuse is not good at all.
 