- Oct 8, 2024
- 3
- 0
- Renault Traffic
Hello!
So I bought in 2021 a Renault Traffic that had been converted to a small motorhome by the previous owner in 2020.
Up until 2023 all was working correctly but since then the fridge has problems turning on (mostly during the night) and it sets off the low-voltage alarm on the inverter. I am struggling to understand the reason why suddenly the fridge is starting to have issues when all was working fine before. The fridge works fine when the engine is running or if the van is parked in the sun and the solar panel charges the battery.
Here is the specification of the equipment used:
- Battery -12V 87.9Ah Gel Dyno europe Dgy12 -80ev
- Solar controller- Victron PWM Light Charge controller 12V-10A
- Inverter 240V- Victron 12/500 VA (Continuous power 400W, Surge 900W)
- Fridge (240V compressor type) - Bomann BS389 42L 70W 84Kwh
- Battery combiner- Victron Cytrix-ct 12/24-120
I have performed some measurements on the system to understand the source of the issues:
Fridge
Whilst the fridge was connected to the inverter in the van, I measured the inrush current and the continuous operating current using a clamp multimeter.
When the fridge is running normally it has an AC current of 0.2A and a 4A inrush current giving a power rating of 46W and 920W respectively (note the fridge is rated at 70W). For me the inrush current seems very high for a mini fridge, most articles I found on the web indicate that the inrush current is 4-10 times the rated current. In this case its around 20 times higher!
Could there be an issue with the fridge causing it to have such a high inrush current?
Battery
I purchased a battery tester and connected to the auxiliary battery. According to the battery spec the CCA at 0C should 600a with an internal resistance of 5.7mOhm. According to the tester the CCA is 188, internal resistance 13.6mOhm and the SOH is 10% whilst the battery SOC is 98%.
As I understand the battery is pretty much dead- 4 years after being installed.... According to the battery spec it should last 12 years!
Is this because the previous owner installed a gel battery directly to the main battery via a Citrix - ct battery combiner rather than using a DC-DC converter that provides the correct charging regime to the gel battery (like the solar controller) ? Should I replace then this equipment?
Other thoughts I had but so far discarded as everything worked in the past
I am a bit of a loss at what to do next, and if I should:
As these modifications are quite costly, I was hoping to get some advice before going any further. Thanks in advance for your support!
- The electrical setup includes a 12V auxiliary- gel battery which is charged via a solar panel (and its controller) as well as Citrix- ct Battery combiner (connected to 12v starter battery).
- The 12V auxiliary battery powers various LED lights, USB sockets, 12V cigarette lighter, and an inverter which powers a 240V compressor fridge. There are usually no other devices connected on the 240V circuit.
Fridge
Battery
- The inverter cannot support the surge current of 920W
- The wires between the battery and the inverter are too thin and are not of the minimum required AWG to support the current surge.
- Replace the inverter with say a Victron/800 VA (Continuous power 650W, surge 1500W)
- Replace the fridge (as its faulty)
- Change the wiring for a more suitable AWG.
- Replace the battery
- Replace the citrix ct battery combiner with a DC to DC converter such as this one: https://www.victronenergy.com/dc-dc-converters/orion-tr-smart-non-isolated